Where does it state cable size is 16mm?
Zs = Ze +(R1+R2)
If= Uo/Zs
should you not be using the Zs (0.44) and not Ze (0.11)? this should bring it down to about 2.8mm ( use 4mm) its just that 16mm2 looks a little big for a 20A circuit0.44192 ohms
Zs: 2.73 ohms
The first bit is OK with some overkill on the currents and cables but compliant and workable.
For the second why have you used 0.4s as the trip time with a fault current of 2090A?
Your cpc size would usually be expected to be smaller than your line conductor csa when using the adiabatic equation.
You are told it is a 16A circuit, you are not given the design current, if you specify a type B 16A BSEN60898 then maximum Zs @70°C is 2.73Ω
Ze is 0.11Ω, therefore R1+R2 must be less than 2.62Ω @70°C.
From the installation method (singles in conduit) and assuming maximum current as you do not have the design current, the cable minimum cable csa is 2.5mm².
If you choose 2.5mm² for the cpc size the resistance R1+R2 is much lower than 2.62Ω so Zs will be compliant.
and then calculate using the rearranged adiabatic equation from 434.5.2
t = k²S²/I² = 115²*2.5²/2090² = 0.019s if the circuit breaker will disconnect in that time then the cpc is OK.
You can also check at the end of the circuit to find 0.3s which is also OK.
From table 54.7 a 2.5mm² conductor is OK, so however you calculate the adiabatic equation it should come out as suitable.
You can't put 2.5mm² into an equation, square it multiply it and divide it and then reverse the process to get the same answer you put into the equation as it is meaningless. e.g. 2.5 *3 /10 = 0.75... 0.75 *10 / 3 = 2.5
As this is a project you should need to do some research for it and perhaps get I²t values for your breakers.
In essence the adiabatic equation is fairly pointless without these values unless you are checking very low fault currents.