Hi,
I have just completed the installation of a defibrillator cabinet and it is wired as follows
Existing 32A final ring circuit on tybeB RCBO.
Addition . FCU spured off a socket outlet, about 300mm of singles.
3A fuse BS1361, about 10m of 1.5 3core swa to an external IP56 junction box.
Obviously testing r1 and r2, Zs, IR etc of the circuit to the JB, using the max Zs values for a 3A BS1361.
But here's the question. Would it be MEIWC or EIC?
My thoughts are EIC as it's a new OCPD and therefore a new circuit. Comparable to a sub main feeding a DB with that feeding the new circuit.
What do you guys think?
Cheers