if you add a light on to a circuit do you IR test the whole circuit or just the cable you install?
if you add a light on to a circuit do you IR test the whole circuit or just the cable you install?
As Andy said..wont 500v blow the bulbs unless disconnected trannys bulbs etc or test at 250v ??
with l-n shorted, there is no voltage accross the transformer (expect to earth, but transformers are DI anyway)wont 500v blow the bulbs unless disconnected trannys bulbs etc or test at 250v ??
1: yesis it ok to do l&n to earth on the lights after a consumer unit change so all the bulbs dont have to removed. if so, what would be written on the EIC (niceic version)? cheers wayne
yes. if he asks why L-n to E, just explain its to avoid damaging any load that may be connected to circuitThanks andy. is this 100% alright, ie infornt of an elecsa assesor.