5.2 The use of additional earth electrodesWhere the resistance of a single electrode is unacceptably high, a number of such electrodes may be connected in parallel. Clause 10.2 of BS 7430: 1998 states that where a number of vertical rod or pipe earth electrodes are so connected, the combined resistance is then practically proportional to the reciprocal of the number employed, provided that each is situated outside the resistance area of any other. The same clause states that, in practice, it is often assumed that such rods or pipes are outside of each other
Are you sure it does? To quote your quote:which in summary says...
not less than the depth of one spike..
but no major advantage going greater than 2x spike length!
it is often assumed that such rods or pipes are outside of each other
you need to turn test kit on...Fiat, I don't envy you with that kind of ground . I put 5 rods in soil linked together and still had no reading. No idea why .
Your meter was turned off?Fiat, I don't envy you with that kind of ground . I put 5 rods in soil linked together and still had no reading. No idea why .
Would concur with "electrivet" on that - distance of BOTH spikes into account methinks??????Are you sure it does? To quote your quote:The way I read that is if you drive 2 X 1 meter rods in they need to be 2 meters apart?
:|
Connection of remote ground grid and adjacent grounding facilitiesThis raises the question , after wanging 1000 rods in and still getting carp reading what does one do? I spent a day on those rods , in the end I kept it TT but used the incoming cable sheath ( 14 ohms)
erm....Are you sure it does? To quote your quote:The way I read that is if you drive 2 X 1 meter rods in they need to be 2 meters apart?
:|