I have a circuit consisting of a single pahse 230v radial circuit serving 3x 2kw fan heaters. 2.5mm squared pvc single core cables instaled in pvc conduit and metal trunking clipped to the surface. A single phase consumer unit with 20A mcb protection. Other info provided is: measured earth fault loop impedance is 0.57 ohms and the measured prospective fault current is 0.4kA.

What other other info do i need to undertake cable calcs? am i right in thinking its just the 4 factors plus cable length? - ambient temp, grouping, insulation and type of protection?

How do i work out the expected voltage drops and the current at each load? - what is the formulae?

Thanks

Andrew McEvoy

 
Volt drop is per amp per meter..

using 6E2 on page 133 of on site guide it has values for all standard cable sizes.

you can see 2.5mm is 18mV/A/m

so if your circuit was 28m long and was taking the full 20amps at the furthest point, the volt drop would be:-

(18 x 20A x 28m) / 1000 = 10.08v

you dived by 1000 cus the 18 is in miliVolts.

so to do your calcs we need some lengths?

Spec Loc. :)

 
if you have your R1 + R2 you can calculate the length aswell.

 