Do you really want the conductors between the transformers and the switchboard to be PEN/CNE? You'd have to class the installation as TNC-S then, and that is likely to cause you some headaches in terms of bonding conductor sizing and exporting earths to cabins, car chargers, etc
Plus once you have created your separate neutral and earth by putting the link in and connecting onto the LV electrode, if you then connect neutral to earth later on, that would run into difficultly with ESQCR as you can't connect neutral to earth legally within an installation, if the only link is placed in the main switchboard then the conductors prior to this point are simply transformer unloading tails, the concept of neutral and earth starts from where you tie down to the LV earth and branch out into separate neutral and earth conductors
One of the reasons for locating the N→E link at the switchboard is so Restricted Earth Fault protection can be utilized.