A builder mate of mine asked me to quote for a new school he was building, I gave him a detailed quotation to present to the owners and the requirments for the supply.
The school is quite small, single storey and consisted of main hall six classrooms and store with male, female toilets and disabled toilet.
The supply is 45 meters from the main hall and the customer requested a total of 47 strip lights, and 47 sockets distributed throughout the building.
I asked for a three phase supply because of the lighting load and harmonics.
I told him it should be wired in lsf cable with cable management to ease future maintenance etc etc. Sockets where to be wired in 4mm and lighting in 2.5mm because of the length of runs voltage drop and load.
The owners decided the quote was too expensive and got an electrician to wire it.
The builder who knows I do thing right was a bit concerned and asked me to look at what had been done.
The electricians had used 2.5 for the sockets even though the out run and in run was 35mts, he had clipped them to the ceiling joists under 300mm of insulation. The lighting was in 1.5 again clipped to the ceiling joists, and told the owners 100 amp single phase would be ok because the maximum demand would only be 40 amp.
I just shrugged my shoulders and told him if it was a house I would say he was a neat and tidy installer, if he is registered I would eat hay with a donkey.
He has 70 meters of 2.5 flat pvc twin and earth running to the sockets without the link from socket to socket!
47 cat two double strip lights on 1.5 cable on a single phase!
I never saw the emergency lighting or the fire alarm god help those kids is all I can say.
The school is quite small, single storey and consisted of main hall six classrooms and store with male, female toilets and disabled toilet.
The supply is 45 meters from the main hall and the customer requested a total of 47 strip lights, and 47 sockets distributed throughout the building.
I asked for a three phase supply because of the lighting load and harmonics.
I told him it should be wired in lsf cable with cable management to ease future maintenance etc etc. Sockets where to be wired in 4mm and lighting in 2.5mm because of the length of runs voltage drop and load.
The owners decided the quote was too expensive and got an electrician to wire it.
The builder who knows I do thing right was a bit concerned and asked me to look at what had been done.
The electricians had used 2.5 for the sockets even though the out run and in run was 35mts, he had clipped them to the ceiling joists under 300mm of insulation. The lighting was in 1.5 again clipped to the ceiling joists, and told the owners 100 amp single phase would be ok because the maximum demand would only be 40 amp.
I just shrugged my shoulders and told him if it was a house I would say he was a neat and tidy installer, if he is registered I would eat hay with a donkey.
He has 70 meters of 2.5 flat pvc twin and earth running to the sockets without the link from socket to socket!
47 cat two double strip lights on 1.5 cable on a single phase!
I never saw the emergency lighting or the fire alarm god help those kids is all I can say.