I've been doing some work on a residential site (posh twin unit mobile homes) and have been asked to go to another site..
Now this site is 3ph TT with BS88 fuses supplying 2 sub DB's which then supply the units/lodges via BS88 fuses again.. now all cabling in underground SWA and each unit/lodge has 100mA RCD protection (not TD) in the meter cabinet and 30mA in the CU..
Now as the sub mains are not RCD protected and this is a TT installation I would say that RCD protection is required or the supply needs to be changed to TNS??
Just after some confirmation that I'm correct:Blushing
From a personal POV I'd say that a RCD incommer is a no go as 1 unit could trip out the whole site.