Lee Sparks
Member
Hey guys,
Quike query.
I helped on a EIC testing & inspect the other day.
When we filled out the green contractor niceic EIC, i noticed that there are two boxes to state the Ze of the installation.
I wondered why there is two boxes?
One box for Ze in "supply characteristics" and the other in the "Particulars of installation at the origin".
I have not noticed this on other certs.
The electrician that was filling out the cert was testing the whole house as he changed the fuseboard and needed to do the cert and asked if i would like to attend. I jumped at it.
He filled out the two boxes in the end, the 1st box he stated the Ze measured at the main intake position then the 2nd box was stated the Ze measured from the main switch at CSU and earthing conductor.( the way im familiar with)
Hope someone can clear this up, cause it threw me.
Lee.
Quike query.
I helped on a EIC testing & inspect the other day.
When we filled out the green contractor niceic EIC, i noticed that there are two boxes to state the Ze of the installation.
I wondered why there is two boxes?
One box for Ze in "supply characteristics" and the other in the "Particulars of installation at the origin".
I have not noticed this on other certs.
The electrician that was filling out the cert was testing the whole house as he changed the fuseboard and needed to do the cert and asked if i would like to attend. I jumped at it.
He filled out the two boxes in the end, the 1st box he stated the Ze measured at the main intake position then the 2nd box was stated the Ze measured from the main switch at CSU and earthing conductor.( the way im familiar with)
Hope someone can clear this up, cause it threw me.
Lee.