boltonsparky
Senior Member
I went to connect up a cooker today for an elderly couple.
I removed the consumer unit cover to carry out an r1 + r2 test on the cooker circuit and to my amazement found there was no main earth from the consumer unit to the MET!!!
The only cables in the earth terminal in the consumer unit were the cpc's.
I took a reading and got 0.14ohms between incoming live and the earth terminal in the consumer unit, so at least they had got an earth but obviously through another path and probably an insuficient one to take a big fault current.
I asked the customer when he'd had his consumer unit changed as it was a newish one, he told me it had been in for three years and was installed by an electrical contractor.
I immediatly installed a 16mm earth conductor.
I'm still amazed an electrician could be stupid enough to forget this or not have the concience to not install it deliberatly.
Just as I think Ive seen it all something else even worse crops up!!!
I removed the consumer unit cover to carry out an r1 + r2 test on the cooker circuit and to my amazement found there was no main earth from the consumer unit to the MET!!!
The only cables in the earth terminal in the consumer unit were the cpc's.
I took a reading and got 0.14ohms between incoming live and the earth terminal in the consumer unit, so at least they had got an earth but obviously through another path and probably an insuficient one to take a big fault current.
I asked the customer when he'd had his consumer unit changed as it was a newish one, he told me it had been in for three years and was installed by an electrical contractor.
I immediatly installed a 16mm earth conductor.
I'm still amazed an electrician could be stupid enough to forget this or not have the concience to not install it deliberatly.
Just as I think Ive seen it all something else even worse crops up!!!