Since no one has objected to 2.5mm cable, I am
assuming it is ok.
I think your assumption is incorrect..
and didn't read my earlier post..
With regard to your question about 2x 2kw heaters it is impossible to answer as you haven't given us the full circuit characteristics or loading of the existing circuit..
WHAT exactly does the existing circuit supply?
How long is the circuit?
What is the spec of the current protective device?
How close to the max permissible earth loop impedance will the amended circuit be?
etc..
You appear to assume every time a fault occurs a fuse trips and you just re-set it...
(Bit like assuming the only fault you get with a car is a flat tyre.. way to simple)
There are numerous other symptoms that overloaded circuits can cause..
such as damage to insulation on a parts of the circuit that is difficult to access causing earth leakage and inability to reset RCD's..
Damp, ingress into poorly installed external components can allow continuity between earth & neutral..
which with prevent any RCD supplying that circuit from being reset..
IF you have multiple circuits sharing that RCD.. you will lose power to more than just your garden..
Wiring regulations requires circuits to be designed to minimise inconvenience in the event of a single fault.
and as 3kw immersion heaters regularly cause overheating faults to 13A rated spurs..
so 4kw worth of heaters on top of whatever else the circuit is already supplying is bad design in my book.