Eagle497
New member
Is it acceptable to over-size the feed cable to a 20A 230V lighting circuit to overcome volt drop ?
The circuit would be :-
20A type B RCBO protecting 100m x 16mm 3 core SWA connected to 3 x 100m, 4mm lighting circuits.
I know that I could treat the 16mm SWA as a sub-main and fit a small distribution board for the 3 x 4mm circuits but it would be at high level and resetting tripped breakers would be problematic.
If the above is acceptable, how should I record the cable size on the installation certificate ?
The circuit would be :-
20A type B RCBO protecting 100m x 16mm 3 core SWA connected to 3 x 100m, 4mm lighting circuits.
I know that I could treat the 16mm SWA as a sub-main and fit a small distribution board for the 3 x 4mm circuits but it would be at high level and resetting tripped breakers would be problematic.
If the above is acceptable, how should I record the cable size on the installation certificate ?