But the crucial thing in this case, is the building inspector inspected the cables prior to being covered.You do need to be clear about the difference between an electrical certificate and a condition report:
When any new circuits are installed an "Electrical Installation Certificate" (EIC) should be issued. This has a signed declaration for design, install and testing of the installation, stating compliance with wiring regulations. It covers all aspects of the new circuits. This is the certificate that the LABC would normally need to see to sign off the work. It has to be signed by the person(s) who have designed, installed and tested the work.
Whereas an "Electrical Installation Condition Report" (EICR) is just a report on the condition of the installation based upon a random sample evaluation of parts of the circuits. It is not a certificate and it does not cover areas that are no longer accessible. (buried cables etc.) This is the only report that can legitimately be done now by contractors who were not involved in the original work.
Wiring regulations and the format of certificates and reports change over time. The current forms are different to the ones that would have been issued in 2006. I doubt any competent electrician would issue an EIC for this work now.
Doc H.
So common sense suggests the combination of that inspection of the cables routing, and the EICR would be enough.
The trouble is LABC don't seem to do common sense in this instance.