pfc on a domestic tn-s setup has come in at 4.6ka is this to high? its the highest ive ever had.
The PFC will be inversely proportional to the Ze..pfc on a domestic tn-s setup has come in at 4.6ka is this to high? its the highest ive ever had.
That is food for thought indeed sellers.4.6 is fine, You may have seen my thread the other day, I got 20ka which made me think.
BRB Pg 76The PFC will be inversely proportional to the Ze..i.e. When Ze is lower and better then PFC gets higher.
so your (4.6ka )4600amp PFC would imply a Ze approx 230v/4600a = 0.05ohms
This would typically imply a TN-C-S rather than TN-S
unless you do have a real good earth and close to transformer?
What reading were you getting for Ze?
Either way 4.6ka in itself shouldn't be a problem providing your breakers are upto the job..
you can check this on pages 56 & 57 of On-Site-Guide,
Read from about half way down page 56.
bullet point i Prospective fault current
and ref table 7.4 on page 57.
:coffee
Whats it like down in the South Atlantic this time of year?Not a problem, i had 12.1 kA yesterday (in St Helena ) and with Ze= 0.04 Ohm and 1361 type II. Its ok.
er... MCB's are designed to break a fault current. an advantage or an MCB is it can be reset, if its not damaged by breaking the fault. even if it does break and need replaced after breaking its rated current, its done its job.so yes the mcb will handle it, but in my eyes an mcb is a resettable device and should be capable of doing so after a short circuit.