Ok. so what is the difference between the DNO "exporting" "PME" to your house, and you "exporting" it to your shed?? Errrr, none. none whatsoever....
First off; Why the requirement [by law] for the DNO to provide PME and not just TNCS, [Do not believe me?? then try reading the ESQCR] This is because of the dangers of a lost neutral, the more earth rods that are installed [thus making it PME] the lower the voltage rise on the neutral, and henceforth the DNO supplied earthing terminal, in the event of a fault, [obviously a good thing]
So what is the problem with TNCS?? Well, the problem [leaving aside "lost neutrals"] is this. As your earth is connected to the neutral, you will find that a PD exists between the earth terminal, and "true" earth, that is equal to the volt drop across the neutral conductor that appears between "your" bit, and the transformer that supplies the thing.
Ok, in your house, this is assumed not to matter, as all extraneous parts are bonded to the MET, so no PD, but what happens the second you step outside, [onto the lawn say] whilst holding your class one appliance?? You could very well find there is a PD then!!
[and no, the rod the DNO installed at "their" end of the service cable will not make any difference at all, as, in general, it will be too far away to bring the mass of earth outside your back door up to the same voltage as that which MAY [in theory] appear between the DNO earth and "true" earth.]
So you "export" the TNCS supply to your shed. So what??? You step outside the shed holding your class one tool, and it is no different at all, to stepping outside the back door of the house. Where is the problem??
Now, if you want to eliminate this problem, you could of course bang in rods all over the place and this will create a zone where the "true" earth will tend to rise up to match the "DNO" earth, so now we can live happily ever after, and run about our lawn in sheer bliss whilst holding our ancient Black and decker drill!!!! JOB DONE!!!!
Yes!! job done!!, [assuming that is] you do not mind the fact that your earthing and bonding system could now very well end up being used as the neutral conductor for half the street.....
Ok, next idea!! We will TT the shed!!!! Yes, great, but now your earth fault protection depends ENTIRELY on the most unreliable piece of electrical apparatus there is, namely an RCCB... So yes, you could TT the shed, but i hope you have either; 1, good life insurance, or 2, a load of RCD's in series to provide redundant protection....
BUT, guess what?? You have TT'ed the shed, you have installed 200 RCD's in series to provide the ultimate in "redundant protection"..... So what could possibly go wrong now!!!!! Errm, well, if your shed earth rod is within about 30 feet of anyone else's rod, or any metallic services, then your extraneous parts in your shed will just, once again, tend to rise to the same voltage above true earth, as the DNO TNCS supplied earth was in the first place....
You have gained precisely nothing....
john......