I think just putting a warning notice on you would be far easier! :^Oyou better start putting warning notices on all your double sockets from now on then you pair of plonkers
No i dont think the IEE will HAVE(not of) made a mistake only you.A 'socket outlet' is the entire socket whether it is a one or two gang design. If you read the MK specification guide you will find that they state 'maximum load' as 13A!Even the 3 way sockets are 13A maximum (they even include a 13A fuse to ensure you cannot overload the socket). By your 'logic' it should be able to handle 39A! And the four way ones could pull 52A.
Let us take the following situation. A 2-gang socket outlet is taken from a ring main as an unfused spur, the cable supplying it is T&E 2.5mm (a common situation). If you loaded that socket with 26A, then unless you are using a 'clipped direct' installation method, you will pulling more current than the cable can handle (Table 4D5). And even if it was 'clipped direct' then you are 1A below the maximum current carrying capacity of 2.5mm T&E.
Somehow I don't think the IEE will of missed that mistake! Because if they did then there is going to have to be a lot of unfused spurs being ripped out of houses up and down the country!
If you did phone up MK then I don't think the guy was laughing at me was he Nicky?
Hello Admin can you edit mr sworlds message like you did mine cos I am deeply offendedI think just putting a warning notice on you would be far easier! :^O
Ooooooh Very authorative Mr Smithmr tesla .mr sworld attempted a joke .
ANY further offensive posts from any member will be removed .
mr smith .
As I've said nicky, I would reasonably expect a double 13A socket to supply more than 13A.does this mean we can use 15A rated juction boxes on a ring then if we can use 13Amp rated sockets? :|
:| (is it ok to 'scoob' the don?)customer must decide what plug rating and what fuse rating he needs for his intended duty.
Thankyou ApacheGood article. :|
(is it ok to 'scoob' the don?)
therefore double gangs are 26A, otherwise no need for except statement re 3 gang? ?:|TECHNICAL SPECIFICATIONElectrical
Voltage rating:
250V a.c.
Current rating:
13A per socket outlet
(except 3 gang which is 13 amp in total)
They may say that but and possibly they could handle that load for a short time but I would not advise it. As said in an earlier post I read an article that suggested using 13 amp single sockets on temporary installations ie building sites so sockets where not overloaded. I have tried to find it but have not.Page 2 of this tech sheet for MK logic plus...http://www.farnell.com/datasheets/36688.pdf
left hand side
therefore double gangs are 26A, otherwise no need for except statement re 3 gang? ?:|
This I would suggest concurs with Nicky's earlier post! {post#36}
(Although there are areas I agree to disagree with Mr T. on..
to tape or not to tape .. that is the question! ; \
26A for a double socket is what MK suggest for their Logic Plus range )
I have a picture illustrating the results of the above problem...On the subject of heating I found the following article from the ASTA BEAB site, it may be worth noting that the fuse in the plug, will contribute significantly to the heating of the socket.Overview: The rules for British Plugs - Simplified
01/02/2006.........
The presence of the fuse inside the plug causes a problem! The fuse gets warm or hot in normal operation - the word 'fuse' means 'melt'. It must get hot - and this is normal. When the fuse gets hot so must the plug itself. The plug then gets even hotter because of the electrical connections inside the plug. For a non-rewireable plug the connections are usually crimped. The British Standard limits the maximum temperature rise in the plug to 52oC above ambient. The fuse has already taken up part of the permit temperature rise. That is why it is so important to make the best possible crimps and keep the temperature rise at these joints to a minimum.
Legally I doubt they could print it in a Tech Spec if it was not a load that could be sustained for a reasonable time!They may say that but and possibly they could handle that load for a short time but I would not advise it. As said in an earlier post I read an article that suggested using 13 amp single sockets on temporary installations ie building sites so sockets where not overloaded. I have tried to find it but have not.Batty
Is it not the plastic front going black and charred that is limiting?Legally I doubt they could print it in a Tech Spec if it was not a load that could be sustained for a reasonable time!As far as I can remember the internal metal track bars inside a socket are actually much greater in size that 2.5mm!
which would be the prime limiting factors IHMO?
I would too but only for a short time. However I would also expect a single gang 13A socket to provide more than 13A for a short time. However the continuous load rating is still only 13A.As I've said nicky, I would reasonably expect a double 13A socket to supply more than 13A.
But that can happen if the (physical) connection to the fuse is not sound Specs.I have a picture illustrating the results of the above problem...{I like pictures }
http://i291.photobucket.com/albums/ll306/SPECIALLOCATION/CLOSEUPOFMELTING.jpg
This was a Tumble Drier plug!! :|
Note it is the Live, Fuse side pin that got hot!
As Apache says..
Very good article!Applaud SmileyApplaud Smiley
{bet you had your boys working hard to type all that out! :^O :^O}