Mr Sworld
Electrical Technician
- Joined
- Mar 21, 2008
- Messages
- 1,152
- Reaction score
- 0
I've always been of the opinion that a 'socket outlet' does not refer to the amount of actual socket points on the front plate but rather the whole item. Hence, as this tread started off with, a double socket is one point of utilisation not two. If you used a dual back box, such as this then you can mount two 1-gang 13A sockets side by side which can handle 26A as the are now two points of utilisation.Page 2 of this tech sheet for MK logic plus...http://www.farnell.com/datasheets/36688.pdf
left hand side
therefore double gangs are 26A, otherwise no need for except statement re 3 gang? ?:|
This I would suggest concurs with Nicky's earlier post! {post#36}
(Although there are areas I agree to disagree with Mr T. on..
to tape or not to tape .. that is the question! ; \
26A for a double socket is what MK suggest for their Logic Plus range )
I'm sorry but I see this mistake all the time. I have a lot of catering companies who cater for bands on tour. The first thing they do in the morning is start plugging in tea urns to make tea and coffee for the crews. As they think that each 13A socket on a double socket can handle a 3kW boiler they plug two of them in.
Within an hour I'll get a call that there is a strange burning smell coming from 'somewhere', bear in mind that we are wired in 4mm for the ring main due to licensing requirements superseding IEE requirements. I have had to cut off both boilers at the plug and then remove and swap the double socket for a new one because the plugs and socket have welded/melted themselves together!