Hi -
My friend it looking at having an 2.2kW Electric (5.2kW heat) multisplit inverter-type AC installed. The unit spec has a max-current listed of 14.6A, and has 20A fuse (attached). The nominal running current for the unit is expected to be 5A, and the Daikin data sheet for his configuration suggests a peak of 9.9A (attached).
The outdoor location has a standard readily accessible 2.5mm socket ring off a 32A MCB. Running a new connection to the consumer unit looks very disruptive.
The installer has said that it's against the regs to run the AC off the ring as a spur. Stating that 13A is the maximum single item device and as the device has a 20A fuse this is against the rules. Instead they are proposing 2x external units both under 13A peak instead. This seems somewhat counter-intuitive and wasteful in terms of space / equipment.
I (personally) have the 9kW Daikin installed in my property which the installers ran with 4mm SWA cable, and I've never seen it use more than 2kW! Usually it runs at 400W - 800W.
Do the rules specifically prohibit running a >13A appliance off a 32A ring - even if the data sheet suggests it won't exceed 10A?
Many thanks,
James
My friend it looking at having an 2.2kW Electric (5.2kW heat) multisplit inverter-type AC installed. The unit spec has a max-current listed of 14.6A, and has 20A fuse (attached). The nominal running current for the unit is expected to be 5A, and the Daikin data sheet for his configuration suggests a peak of 9.9A (attached).
The outdoor location has a standard readily accessible 2.5mm socket ring off a 32A MCB. Running a new connection to the consumer unit looks very disruptive.
The installer has said that it's against the regs to run the AC off the ring as a spur. Stating that 13A is the maximum single item device and as the device has a 20A fuse this is against the rules. Instead they are proposing 2x external units both under 13A peak instead. This seems somewhat counter-intuitive and wasteful in terms of space / equipment.
I (personally) have the 9kW Daikin installed in my property which the installers ran with 4mm SWA cable, and I've never seen it use more than 2kW! Usually it runs at 400W - 800W.
Do the rules specifically prohibit running a >13A appliance off a 32A ring - even if the data sheet suggests it won't exceed 10A?
Many thanks,
James