the spur current (and fuse) can be up to 20A
you can't get a 20a fuse for a spur
the spur current (and fuse) can be up to 20A
https://uk.rs-online.com/web/content/discovery/ideas-and-advice/fused-spurs-guide#you can't get a 20a fuse for a spur
BS1362 fuses (that would be used in a fused spur) only go to 13a. if you do find a 20a BS1362 fuse then its a fake fuse that probably won't blow
Try the fused spur with a 13amp fuse, if it pops the fuse on a regular basis then you need the dedicated feed, if it runs ok then youre sorted.BS1362 fuses (that would be used in a fused spur) only go to 13a. if you do find a 20a BS1362 fuse then its a fake fuse that probably won't blow
No it is not a reg. It is in the on site guide and is someones personal recommendation only.It is a regulation recommendation that any electrical device greater than 2kw is connected via its own circuit.
Whilst the item may run at lower than this there are times that it would run at or near too it’s max.
Under what reg no would it not be compliant?if MI's require minimum of 15.8a then it'll need its own circuit. would it work on a 13a spur? probably. would it be compliant? no
Ok thanks. FWIW I think binky's point is right, the spur current (and fuse) can be up to 20A particularly if the appliance isn't expected to use this much current for long periods.
View attachment 15620
Ok Boris; let’s say that Bs7671 are the regs and the On-site Guide is considered as an influence towards best practice, so if you wish to choose an alternative method feel free, it’s your design not mine. I just think that it is generally easier to follow best practice as saves a lot of unnecessary questions should an issue arise.No it is not a reg. It is in the on site guide and is someones personal recommendation only.
I have to say I regard the OSG as dumbed down regs and not overly worth looking at.Ok Boris; let’s say that Bs7671 are the regs and the On-site Guide is considered as an influence towards best practice, so if you wish to choose an alternative method feel free, it’s your design not mine. I just think that it is generally easier to follow best practice as saves a lot of unnecessary questions should an issue arise.
Typical incorrect manufacturers blurb. The 20 amp one is a flex outlet plate with no fuse.
Typical incorrect manufacturers blurb. The 20 amp one is a flex outlet plate with no fuse.
they aren't fused just rated for 20Amp loadBelow is from their web page , as has been said before they do not make BS 1362 20A fuses, RS have listed it wrong ,
20A Double Pole Control Switches
The MK Electric Albany Plus range of switches features stylish curved design, the double pole switches are manufactured from the finest materials and maintain their high quality appearance for years to come. The terminals in the back of these 20A switches have a funnel entrance and are upwards facing, to make installation easier.
yes I agreethey aren't fused just rated for 20Amp load
You can do this , as long as the load is 20Amp or less ( cable needs to be the same as the ring, (remember the fuse is there to protect the cable not the appliance))The last one of these I saw was spurred off the socket circuit with no OCPD other than the 32A MCB
You can do this , as long as the load is 20Amp or less ( cable needs to be the same as the ring, (remember the fuse is there to protect the cable not the appliance))