Hello all,
I have changed a C/U and have a problem with the lighting circuits. Basilcally the landing area light has a live fed from the downstairs lighting circuit but takes its neutral from the upstairs lighting circuit. This is a problem for me to comply with 314.1 as I need to put them both on the same RCD (dual RCD board fitted). I am going to use this job for my surveilance visit for my scam membership as have also wired the extension and a couple of other jobs but am a bit concerend about not complying with the above reg. What do you guys reccomend - a note on cert? Or is rewiring that light the only alternative - bit impractical though.
Any advice welcome.
Thanks
I have changed a C/U and have a problem with the lighting circuits. Basilcally the landing area light has a live fed from the downstairs lighting circuit but takes its neutral from the upstairs lighting circuit. This is a problem for me to comply with 314.1 as I need to put them both on the same RCD (dual RCD board fitted). I am going to use this job for my surveilance visit for my scam membership as have also wired the extension and a couple of other jobs but am a bit concerend about not complying with the above reg. What do you guys reccomend - a note on cert? Or is rewiring that light the only alternative - bit impractical though.