Maybe I'm being extremely dumb here but I need some advice please as I'm missing something.
I've installed a ring final in a bungalow. 1970s Mcleans job with lots of paramount walls. Service is PME.
Tested the ring and its spot-on at every socket. Connect the power and test earth loop and the readings increase the further from the board I get.
So I go back and test again. R1,-R1, R2-R2, Rn-Rn at the board then R1+R2, R1+Rn, R2+Rn at each socket. Everything matches up.
Test continuity for every cable down the back wall where the readings are highest and everything is fine.
Connect everything up, power up and the earth loop still reads like 2 radials not a ring. I get 0.28ohms at the nearest sockets and 0.56ohms at the furthest.
Can anyone explain this to me ????