Gn96
Member
Bare with me people as I try to explain this. Currently working on a site, been responsible for testing under floor power tracks that are fed in 3 core 10mm swa on 32a mcb. Tested a bunch of them maybe 4-5 weeks ago. Got the results all happy days. In work this week I was informed a separate company is employed by the main contractor to “witness” me testing circuits I have already tested to “confirm the same or similar readings” which the main contractor wants as confidence the testing is being done correctly. So example 1. 1no of power track tested weeks ago Recorded R1 R2- 0.27. These have not been powered up yet so no live testing done. I’ve then tested the same track with the “witness” company and the R1 R2 value is now 0.10 less.= 0.17.
Example 2.
6no of fan coil units supplied in 2.5mm singles in 25mm galv conduit. End of line reading R1 R2 - 0.65. Tested last week. On to this week re testing the same circuit with the “witness” the current R1 R2 value is 0.55.
So got a few funny looks from the two men who work for the witness company and questioned why it was lower like I was in a police interview. I always test correctly as it’s my name signing the test sheets and I’m liable so never blag test readings as some people do. The only explanation I could possibly give them is 1. Other circuits have now been connected running in the same containment and fan coils being connected up, which are bolted to the concrete giving numerous parallel paths and as more circuits are connected the earth reading would come down surely? It wouldnt be practical to go around every circuit on the job to disconnect every earth and eliminate parallel earths and then reconnect them again. This explanation didn’t seem to satisfy them and a few huffs and puffs and they left me too it. I’m yet to hear back from their report. Anyone got advice if I’m in the right? I was always told R1-R2s can fluctuate in time. And to be fair the first time these circuits were tested it was -2 on site. Currently it’s 10c, I’ve heard temperature can effect resistance in cable but always took that with a pinch of salt. Let us know what you think lads and ladies
Example 2.
6no of fan coil units supplied in 2.5mm singles in 25mm galv conduit. End of line reading R1 R2 - 0.65. Tested last week. On to this week re testing the same circuit with the “witness” the current R1 R2 value is 0.55.
So got a few funny looks from the two men who work for the witness company and questioned why it was lower like I was in a police interview. I always test correctly as it’s my name signing the test sheets and I’m liable so never blag test readings as some people do. The only explanation I could possibly give them is 1. Other circuits have now been connected running in the same containment and fan coils being connected up, which are bolted to the concrete giving numerous parallel paths and as more circuits are connected the earth reading would come down surely? It wouldnt be practical to go around every circuit on the job to disconnect every earth and eliminate parallel earths and then reconnect them again. This explanation didn’t seem to satisfy them and a few huffs and puffs and they left me too it. I’m yet to hear back from their report. Anyone got advice if I’m in the right? I was always told R1-R2s can fluctuate in time. And to be fair the first time these circuits were tested it was -2 on site. Currently it’s 10c, I’ve heard temperature can effect resistance in cable but always took that with a pinch of salt. Let us know what you think lads and ladies