Testing a radial circuit today and Zs .89ohm x1 rcd 218ms and 202ms and 5x greater than 40ms
TNCS earthing arrangement.Zs .34, Pfc .71. back at house. Circuit no more than 12/15m to outbuilding. circuits from sub board no longer than 15m.
This radial supplying an outbuilding with a swimming pool in it. 2.5mm 3c swa feeding a metal 6 way Board in the outbuilding, glanded straight to the box. :red card . Will be replacing the exported earth with a rod, and rcd-ing at the outbuilding, but my question is why would this be happening.
Gone through all the obvious.
IR on all cables ok.
have 3 rcbo's on new board and only this one playiny up.
Replaced rcbo for a new one and still same problem.
If I rcd test at metal cu trip times as follows on both rcbo's 27/17ms
Any help would be most appreciated.
Macca
TNCS earthing arrangement.Zs .34, Pfc .71. back at house. Circuit no more than 12/15m to outbuilding. circuits from sub board no longer than 15m.
This radial supplying an outbuilding with a swimming pool in it. 2.5mm 3c swa feeding a metal 6 way Board in the outbuilding, glanded straight to the box. :red card . Will be replacing the exported earth with a rod, and rcd-ing at the outbuilding, but my question is why would this be happening.
Gone through all the obvious.
IR on all cables ok.
have 3 rcbo's on new board and only this one playiny up.
Replaced rcbo for a new one and still same problem.
If I rcd test at metal cu trip times as follows on both rcbo's 27/17ms
Any help would be most appreciated.