- Nov 28, 2009
- 14,720
- 891
So a TT system needs double pole mcb's as well then?but surely it must be isolated under fault conditions?
Sorry Dave I misread your post, SP MCB’s are OK.
Its SP RCBO’s that are the problem as they don’t clear a N→E fault. An up front RCD to clear N→E faults would make RCBO’s pointless.
now,
that depends,
30mA SP RCBOs and an upfront TD100mA :C
Exactly, that's why I don't see any point in SP RCBOs,A SP RCBO will clear a L→N fault but not a N→E fault. The DP TD RCD would clear the fault at the same time blacking the entire house out, which circumvents the point of RCBO’s.
I’ve seen 45A flowing through a N→E fault where a combined high resistance neutral and a N→E fault existed. It waspure chancebad luck I found it.
However, I could not find a reg that required disconnection of the N in the event of a fault on a TT.
So, can anyone come up with the reg no please?
I was convinced that it was there, but, I couldn't find it.
. In any domestic installation ALL live conductors must be broken for isolation.
But isn't that just the main switch?
SP or DP makes no difference to me. if you have a fault then it will trip isolating the line, circuit is then dead. everywhere has SP MCB's yet no-one questions them only switching line and not neutral in if tripped due to a fault