is installing rcbos type c bad or good

type b breaking capacity 30amp

type c breaking capacity 60 amps

i would say not to use type c due to cable failing before breaker

your views please!

is it ok to fit type c or not

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
is installing rcbos type c bad or good type b breaking capacity 30amp

type c breaking capacity 60 amps

i would say not to use type c due to cable failing before breaker

your views please!

is it ok to fit type c or not
The type b or c isn't to do with 'breaking capacity'. You can get a 32A rcbo in type b or type c. The type b,c (or d) is to do with inrush currents.

 

paulh

Senior Member
Joined
Jun 4, 2008
Messages
144
Reaction score
0
Type b,c,or d are all acceptable items to be fitted as overcurrent devices period. Perhaps you should elaborate on the circuit you wish to fit these too. After all if you are designing a circuit you will be in possession of all the relevant information.

 

sdon26

Junior Member
Joined
Apr 11, 2008
Messages
10
Reaction score
0
is it ok to fitt a 6 amp rcbo type c if zs under 3.06

 

Admin1

Forum Founder
Joined
Feb 6, 2008
Messages
10,278
Reaction score
-1
Welcome to the forum.

May I ask if you are a Spark?

:)

 

sdon26

Junior Member
Joined
Apr 11, 2008
Messages
10
Reaction score
0
is it ok to fitt type c rcbo 6amp for lighting

if zs is below 3.06 ohms

problem is that wholesaler only has 6amp rcbos wylex

 

paulh

Senior Member
Joined
Jun 4, 2008
Messages
144
Reaction score
0
pass............please see my last post

.....

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
is it ok to fitt type c rcbo 6amp for lighting if zs is below 3.06 ohms

problem is that wholesaler only has 6amp rcbos wylex
The maximum Zs a 6A RCBO can have is 3.09 ohms. However that is at an ambient temperature of 10 degrees centigrade. However if the ambient temperature of that cable exceeds 10 degrees then the Zs will become too high for that RCBO (too high for a type B RCBO as well!).

That Zs seems to be very high for a lighting circuit. What type of supply do you have?

 
Joined
Mar 28, 2008
Messages
13,619
Reaction score
296
is it ok to fitt type c rcbo 6amp for lighting if zs is below 3.06 ohms

problem is that wholesaler only has 6amp rcbos wylex
I presume you are calcing your 3.06 as the 80% of the value from table 41.3 pg 49 Big Red book???

i.e. 3.83 x 0.8 = 3.064.

as Mr S says the O.S.Guide table 2D pg 103 lists max Zs as 3.09

So the actual answer to your question is Yes TypeC 6A RCBO is ok... Also assuming any other relevant correction factors have been applied to your Max ZS. :)

as a rough quick calc... lets say max Zs 3.00.

TN-S & Ze = 0.8 Max R1+R2 3.00 - 0.8 = 2.2

2.2 with 1.0mm T&E is 60.7m

2.2 with 1.5mm T&E is 72.8m

TN-C-S & Ze = 0.35 Max R1+R2 3.00 - 0.35 = 2.65

2.65 with 1.0mm T&E is 73.2m

2.65 with 1.5mm T&E is 87.7m

Again as Mr S said.... those Zs values would be a quite long lighting circuit for a domestic environment??????

whichever earth type and/or cable size used ALL 60m+!!! :eek: ; )

 

jl-heating

Distinguished Member
Joined
Dec 16, 2008
Messages
1,158
Reaction score
0
not much margin for error there, i would be inclined to investigate the circuit, as above, with in tolerance but only just.

can you give us more info on the circuit and earthing arrangements etc..

 