Hello Shamus welcome to the forum...Guiness DrinkNot too sure what you're getting at with that question, but i've just recently bought a large sliding compund saw, with a 2.3kw motor. When i tried starting it, the 16A breaker in my shed tripped, along with the main 20A breaker in the CU in the house. Both breakers were type B. The start up current must have exceeded 20A for it to take out both breakers.I've changed both for type C's and the problem has gone away.
Not sure if this is what your asking, but under normal circumstances i doubt if you would ever notice the difference.
Martyn my wholesaler has no problem getting b type wylex rcbo's. I needed aAs long as you can meet the Zs values for a C curve, it`ll make little difference.I`ve used `em a few times - Wylex don`t seem to have availability on B curve RCBO`s!!!
KME
SL this is why I always put adequate supply into garages and outbuildings at least 32 amp that way you can put ring main for sockets or 32 amp radial.Hello Shamus welcome to the forum...Guiness DrinkJust a simple question.. are your Zs values still ok?
typically the type 'C's are about half that of type 'B'..
e.g.
20A b= 2.3ohm c=1.15ohm
16A b=2.87ohm c=1.44ohm
this would obviously affect the max permissible cable length..
and when you say shed......... is it a long way....
But saying that.... Is it RCD protected anyway? so Zs of less importance.
I think the point the original poster was getting at was generally on domestic we use type B mcb's (as stated higher Zs permissible), but since 17th with added RCD & RCBO's.
Many manufactures only tend to do type C RCBO's.
which is why Oracle was asking for opinions on Type B -vs- Type C
HTH!
Indeed there sir Batt's!SL this is why I always put adequate supply into garages and outbuildings at least 32 amp that way you can put ring main for sockets or 32 amp radial.Batty
Oraclethe reason for the question is 2 fold:On a tt system the zs is too high for any breaker (normally) so to mitigate this you use an rcd - therefore is the type of rcbo relevant anymore?
The second part. If the tt board is using rcd's and rcbo's does the main isolator need to be a time delayed rcd or can it be a simple isolator?
6.
Yes the Zs valuse are ok. The run to the shed isn't that far away and it is rcd'd. I will hopefully be building a new double garage in the near future, and i intend upgrading the entire supply to the garage, and provide a suitable supply for external electrics as well, (maybe a hot tub - if the cost of electric ever comes down.)Hello Shamus welcome to the forum...Guiness DrinkJust a simple question.. are your Zs values still ok?
typically the type 'C's are about half that of type 'B'..
e.g.
20A b= 2.3ohm c=1.15ohm
16A b=2.87ohm c=1.44ohm
this would obviously affect the max permissible cable length..
and when you say shed......... is it a long way....
But saying that.... Is it RCD protected anyway? so Zs of less importance.
I think the point the original poster was getting at was generally on domestic we use type B mcb's (as stated higher Zs permissible), but since 17th with added RCD & RCBO's.
Many manufactures only tend to do type C RCBO's.
which is why Oracle was asking for opinions on Type B -vs- Type C
HTH!
Nicky your phase to neutral will still need to be below tables in regs though to ensure mcb part trips within required times.Type B or C has nothing to do with Zs when used with an rcd or rcbo because the curves are to do with overcurrent protection along live and neutral wires not earth wiring. The Zs on a 30mA rcd can be up to 1666ohms. It is preferred for the Zs to be in normal parameters but it is not essential.
we decided it's 1666.666666666666666666Well said . Although the correct figure is now 1667 , but lets not split hairs
you gotta round the last number to 7 patchwe decided it's 1666.6666666666666666667so it's a rounding issue