I know - that was the point I was makingyou gotta round the last number to 7 patch
As it's recurring I could have gone on with the 6's until I ran out of allowed words
I know - that was the point I was makingyou gotta round the last number to 7 patch
phase to neutral Zs what are you talking aboutNicky your phase to neutral will still need to be below tables in regs though to ensure mcb part trips within required times.Batty
like what? an RCBO has the same tripping characteristics as an RCD, just most RCBO's only disconnect live phase line (whatever it is today), unlike RCDs are DPThe reason to ask about the incomer being a TD RCD, is because the RCBO's (in domestic boards) are only single pole, therefore it is possible to have certain failure situations where it would not trip it.
O.
then if its a TT you MUST use DP RCBOs, domestic or otherwise.Let me rephrase....So Zs's aren't important with an RCBO (aslong as it is below 1666 - but ideally 200)?
Obvious the type determines the tripping characteristics, so could you get way with fitting a C, even though the Zs might not comply (because it's an RCBO) ?
The reason to ask about the incomer being a TD RCD, is because the RCBO's (in domestic boards) are only single pole, therefore it is possible to have certain failure situations where it would not trip it.
O.