went to a pre-fit for a kitchen company i do work for
recent c/u change, no paperwork, 16th board but done in may so no drama, 5+5 split load wylex. 16mm main earth
tns, ze = 0.15, socket outlet zs = 0.44-0.56(spur) l1-l1 = 0.4 n1-n1 = 0.5 r1-r1 = 0.75
rcd trips pressing test button but doesnt trip with meter on rcd test although with trip function disabled on loop test the rcd trips before giving a reading as it should
replaced rcd to no avail.
all neutrals look to be correct,
feel i have missed something obvious but had one of those days so if anyone has any thoughts they will be much appreciated before i contact original spark