AH!Although this
technically only refers to grade E systems, I would still consider it pertinent:
c) The circuit serving the smoke alarm(s) and any heat alarms should preferably not be protected by any
residual current device (r.c.d.). If r.c.d. protection is required for reasons of electrical safety
(e.g. in an installation forming part of a TT system), either of the following conditions should be satisfied.
i) The r.c.d. should serve only the circuit supplying the smoke alarm(s) and heat alarms.
ii) The r.c.d. protection of a smoke alarm circuit should operate independently of any r.c.d. protection
for circuits supplying socket outlets or portable equipment.