Rcd Test Problem
Wattsy
Dec 13, 2009
53
Hi all,
I was doing a pre work survey on a static home today where the owner want a couple of circuits extended.
Its a TT and the Ze was 320ohms which i know is higher than recomended.
Its got an old Wylex board supplied through a 30ma RCCB switch.
I tryed to do and rcd test with my Megger 1553 and it kept coming up with >50v. Which i understand is the touch voltage of the cpc. Can anyone tell me why this is the case.
Any help would be appreciated
Many thanks:)
Have you done an earth loop L-N.
Justa a thought,, if you have a high L resistance combined with a high E, then your touch voltage could be a bit high.. If all tests are OK though and it still won't RCD test, then do the RCD test across Outgoing L and incoming N on the RCD
Have you done an earth loop L-N.Justa a thought,, if you have a high L resistance combined with a high E, then your touch voltage could be a bit high.. If all tests are OK though and it still won't RCD test, then do the RCD test across Outgoing L and incoming N on the RCD
Obviously spot on advice as always Noz but why test across outgoing L and incoming N. You obviously know why but im trying to understand why you do that. Can you explain it to me.
Guinness
It will test the RCD,, just like the test button, but with readings that mean something
and is safer that incomming L and outgoing N as your N probe will always be "live" until you remove the L probe.
doesnt that mean less than 50 volts, as in not energized?
> means greater than
< means less than
Therefore with him saying >50 there is more than 50 volts
The Megger MFT has two touch voltage settings- 25v and 50v.
It can be set to display which setting you have it on during the test.
Are you sure that's not what it is doing, rather than displaying a fault
Hi, I used the socket on my MFT 1553 on the auto setting, it starts the
test then says the touch voltage is >50v. Could this be because the Ze is 321ohms? If so measuring it at the Rcd out L - in N as you said should work but is it acceptable?
Thanks again
Yes you can test RCD where you like, on TT it won't make a lot of difference
The >50 v indicator is warning that the Fault touch voltage would be in excess of 50 Volts so it won't allow you to continue, not sure why at 321oms as 1666.66 ohms would be limit for that at 30 m A. Maybe its preprogrammed to give that out at anything above 200 ohms RECOMMENDED in BRB Pg 50.
If you can reduce the Ze by installing additional Earth stakes then may be You would be able to do the tests.
Unless he has it set on 300mA by mistake. The limit would then be 167ohms would it not. :C
It's definately set at 30mA.
Nozspark, the N - E fault would make sense but when i tested the PFC the PSSC was 1.09kA and the PEFC was showed <1A so would this be the case if the E & N were connected together?
These are all the tests i have done as i didn't have much time at the end of the day yesterday. I will be going back on monday though so if anyone can suggest any more tests i'd be very gratefull.
Its a ring final circuit
Ze = 320ohms
ZS (direct from socket on circuit to be extended) = 321ohms
r1 = 0.63ohms r2 = 0.78ohms rn = 0.62ohms (r2 seems a bit low?)
PSSC = 1.09KA
PEFC = <1A
Calculated cable length = 85m
RCD test from socket
= No result (>50v)
have u done a full polarity check at the incoming supply.... check between L-N, N-E, E-L. if polarity is not correct the >50v can sometimes come up on the meter... L-N could be reveresed...
It's definately set at 30mA. Nozspark, the N - E fault would make sense but when i tested the PFC the PSSC was 1.09kA and the PEFC was showed <1A so would this be the case if the E & N were connected together?
Ze = 320ohms
PSSC = 1.09KA
PEFC = <1A
= No result (>50v)
Hi mate,
Those readings look ok to me.
Your PEFC will be less than 1A with a Ze of 320 ohms - 230/320= 0.72A
This is why RCD is required for for earth fault protection;)
= No result (>50v)
If I'm reading this bit correctly then you shouldn't get a trip result at half X
I've just re-read my instructions and the Megger gives a touch voltage reading on a bar graph (if selected).
You can set the touch voltage limit for RCD testing at either 25v or 50v and it will display the reading with the trip time.
The only time the Megger will display >50v is if you try to perform a 'dead test' on a live circuit. :D
Edited for accuracy:)
Are you sure the megger switch has selected the correct test as sometimes (i read) that when you twist the dial it can sometimes not select perfectly. It could have stuck on a dead test when you thought it was on a live test therefore showing the <50v symbol.
Just a thought
Hi again,
I've just ran some RCD tests with my Megger.
The touch voltage is shown on a bar graph above the trip time - on each of my tests the graph didn't move, but I am testing on TN-C-S.
I must admit, I've never had a case where the set touch voltage (25v or 50v) has been exceeded on my megger, so I can't say for sure what it would display if this were to happen.
As someone mentioned earlier, though, I can't see how the touch voltage can be exceeded with a Ze of 320 ohms when the calculation for a 50v touch voltage gives us 1667 ohms at 30ma
Bit of a puzzler:C:)