Hi, recently did quite a bit of work on a bungalow (DB change, kitchen wired, extra sockets, smokes etc.,). Had some issues with installation but managed to locate faults and everything tested off fine. A couple of weeks later customer contacted me to advise RCD tripping intermittently and when microwave / kettle being used.
I moved the sockets over to the other RCD and everything worked fine - narrowed down to faulty RCD.
Now changed the RCD and it holds on when microwave / kettle being used but when doing auto RCD tests RCD trips but when reset for remainder of tests, doesn't trip. Meter does not show any values. Tried another tester and same happens so not the meter. Redid RCD test but not in auto and same again happens, RCD trips at x1 but meter shows no values.
All other tests come back good (continuity / earth loop etc). Everything connected correctly in DB (ie. neutral links). Just don't know why this is happening with the tester. Same happens when testing RCD on another circuit - that's a brand new circuit and definitely nothing up with it.
Any advice appreciated.
I moved the sockets over to the other RCD and everything worked fine - narrowed down to faulty RCD.
Now changed the RCD and it holds on when microwave / kettle being used but when doing auto RCD tests RCD trips but when reset for remainder of tests, doesn't trip. Meter does not show any values. Tried another tester and same happens so not the meter. Redid RCD test but not in auto and same again happens, RCD trips at x1 but meter shows no values.
All other tests come back good (continuity / earth loop etc). Everything connected correctly in DB (ie. neutral links). Just don't know why this is happening with the tester. Same happens when testing RCD on another circuit - that's a brand new circuit and definitely nothing up with it.
Any advice appreciated.