On testing RCD tripping times all was ok till 5x then it failed
On testing RCD tripping times all was ok till 5x then it failed
Any from past experience proves it is faulty although the tests at the board suggest otherwiseother option is to test at the RCD in the board, and not through a cct - sometimes makes a difference.
Any from past experience proves it is faulty although the tests at the board suggest otherwise
other option is to test at the RCD in the board, and not through a cct - sometimes makes a difference.
not acceptable to say its passed by disconnecting the circuit. you want it to work when the circuit is connected, i.e if someone gets a shock, not for it to work only in 'ideal' conditions with various bits disconnected to make it 'pass'
not acceptable to say its passed by disconnecting the circuit. you want it to work when the circuit is connected, i.e if someone gets a shock, not for it to work only in 'ideal' conditions with various bits disconnected to make it 'pass'
The RCD tests should be tested in isolation.... the continuity and insulation tests verify the circuit
if there is something with the circuit that's stopping a safety device from functioning as intended then do what you want, but i wont be ignoring it 'because the book says to test in isolation'. simple fact is, if the RCD isn't capable of working when a circuit is connected then its not fit for purpose
if there is something with the circuit thats stopping a safety device from functioning as intended then do what you want, but i wont be ignoring it 'because the book says to test in isolation'. simple fact is, if the RCD isnt capable of working when a circuit is connected then its not fit for purpose
if there is something with the circuit thats stopping a safety device from functioning as intended then do what you want, but i wont be ignoring it 'because the book says to test in isolation'. simple fact is, if the RCD isnt capable of working when a circuit is connected then its not fit for purpose
The test currents applied during RCD testing can be adversely affected by a circuits wiring or connected load. Real world loads are generally higher than RCD tester allowable currents. Erroneous results can be encountered if the RCD is not tested as near to source as possible with all loads disconnected as per BS7671. Of course this does not negate the need to test the circuit in isolation as well. ie Ins Res results can also have erroneous results if certain loads or RCDs are still connected.
Doc H
I think a certain Mr @Sidewinder may be interested in your findingsTotally agree if it fails a low level current test on the circuit then how reliable is it going to be with a real fault
You are making an assumption that the fault current may be higher without any guarantee it will be. Anything above 30mA is sufficient to cause serious harm or death, the current situation as extolled by the IET for the testing of RCD's may as well tell us not to bother with RCD's as they may not operate when really needed
The only erroneous problem I have ever found with an RCD tripping at source and not tripping from a test on the circuit was the fact that on ramp test the RCD consistently tripped with a current exceeding it rated value. This was not an isolated case and some were brand new boards and some only a few months old that tested OK at install but not when doing other work some months later
Due to the blame game culture the UK has adopted I always ramp test any RCD I work on for piece of mind even though it is not a testing requirement to do so. The number of times I have found faulty RCD's is backing this approach up, I look at every job as a potential legal case these days if something god forbid happens then I know I have done everything I could do to mitigate any prosecution for negligence
Sharpend is correct, an RCD is tested without any loads connected to comply with BS 7671.You would think so, however the IET tech gurus advised me that You are testing the RCD therefore it should be tested without circuits attached as they may prevent it from tripping, this the rcd isn’t at fault but the fault lies within the circuit.