Hi chaps, wandering if anyone could enlighten me to this,
Doing a rewire and socket fronts for upstairs power are put on. Power on and press the rcd test button and nothing happens.
Tell my boss, and he says 'bet you have a N-E fault. When you have N-E fault the rcd won't trip when no loads are connected.'
So i remove the Neutral in question and the RCD trips on the test button and Sure enough, dead short on N-E on res. I trapped neutral in a back box.
Put the circuit under load and the RCD trips.
So why would having a N-E fault with no load attached stop the RCD test button working????
Thanks in advance.