Hi all this question is doing my poor head in headbang so any help would be fab...Find the cross-tional area of a copper cable 42m long which carries current of 36A with a voltage drop of 2.69V.
If you could explain it to me in simple terms I would be gratefull
Assuming we are looking for one of the "standard" cable sizes not an obscure bit of customised gauge cable....
Then I think one of your values may be slightly out... But anyway... here goes... :|
ALL cable has a resistance value which consumes or "drops" some of the voltage that travels down it and the amount of voltage dropped also increases with current.
There are tables in BS7671 for Volt drop per amp per meter for all of the standard cable sizes..
See page 133 one site guide table 6E2.
because the voltage dropped is very very small the table lists it as:-
"millivolts per amp per meter"
so you need to find out how much of your 2.69volts is dropped per meter & per amp..
Cable is 42m long.
2.69volts over 42 meters is 2.69/42 = 0.06404v per meter.
but this is with 36 amps current..
so 0.6404volts over 36amps is 0.06404v/36A = 0.001778v per meter per amp
convert it to milivolts....
0.001778x1000 =
1.78millivolts per amp per meter
look down table 6E2... g 133 O.S.G. to try and find a match.. ?:|
it can be seen that 25mm CSA has a volt drop of
1.75mV/A/m
so I would suggest it is 25mm copper cable!
calc it back again using the 25mm volt drop figure..
(1.75 x 36 x 42)/1000 = 2.646volts
as said at start that does leave us a 0.044v error!
but its the best I can do! :|