As i said have told customer what is required didnt think i need to go as far as issuing a danger notice. If it was down to me id install a 20a type b rcbo to air on the safe side but you cant make people do thing . Thanks for your input Tech. Cheers.
Tech the pfc and pefc are the same due to tncs supply at origin 230/.32=720amps and that approx the readin im getting.
Tech the pfc and pefc are the same due to tncs supply at origin 230/.32=720amps and that approx the readin im getting.