One earth may not have been able to take the fault current. The whole philiosophy of a ring final is there are two cables in parallel (effectively) to share the load. With one earth disconnected, in the event of a fault (short circuit) that one earth core would be overloaded as it is missing it's partner to share the load.What would the risk be if I had left one earth in? If everything was earthed? Could you plz explain the risk plz? Obviously it's sorted as I found the fault and corrected it but out of curiosity and just help understanding please. Thanks anyone?
Also you have left the other half still with it's N-E fault. I have a suspicion there is more to it than that as why didn't that n-e failt trip the rcd? perhaps the erath on that end was disconnected? who knows, we are not there.