Andy,
All your post is is that of a manufacturer of a service fuse carrier.
This does not prove anything.
The separation point for TN-S/TN-C-S is at the service head.
IF the earth is prior to the head this is TN-S, if it is in or after the head then it is TN-C-S, check the diagrams in the brb.
Barx,
Regardless of the status of the "PME sticker" if the supply is TN-C-S then it MUST be PME, check ESQCR, especially on new installs, there is a time frame for retrofitting, but I thought that this had expired.
We are now discussing STATUTE LAW, forget 7671 that is just peanuts in comparison.
Guys, please check up the brb and more importantly the statutory regs, these cannot be ignored, in the same way that to tamper with DNO kit is a criminal offence.
i.e. it is a criminal offence to pull service fuses, cut seals on fuses and meters, change meter tails DNO side of the meter, fit or remove 951 clamps to DNO cables (apart from that 951 bit being just plain damn stupid).
This is all to do with how the supply is PRESENTED to the installation, not on what your take on this is regardless of measurements it is NOT your decision it is that of the DNO, this is their realm, if we all stuck more to our bit & got the DNO to do their bit then it may be that they would realise the issues out there, but it seems that we (well some of us are) are doing their bit illegally, thus letting them make more profit and hiding the real issues by being criminals.