They are type tested, and the information is given on page 4 from the link you posted.Manator, where did you find it? Can you please give me the link!
You need to look at your protective device upstream of the db, now at a pfc of 16ka how fast will it disconnect, faster than the 10ms probably betwen 2 - 5 milliseconds, so no issues probablyI found pages J65 and J89 but this information is not there. Apparently only available information is that the terminals of this distribution board are rated for 35kA at 10ms. So I am assuming that the bus would also be rated for 35kA at 10ms. I am still however not able to fugure out whether this distribution board can be installed at a location of 16kA prospective fault current?