I got a call from a customer saying his electric shower was tripping the mcb every few days, there was no pattern to the tripping, shower is used every day and sometimes will go 3 or 4 days without it tripping the mcb and other times it will trip eery day or so. Sometimes trips when shower in use and other times between showers.
I have inspected the cable for signs of damage but found none, mcb is a cpn B40 on a dual RCD board. Insulation resistance on the circuit is >299 Mohms between L/N, L/E, N/E. R1 + R2 is o.21 ohms. Zs 0.71 ohms. I checked the pulll co isolator and it showed some signs of heat damage, so replaced that which resulted in the shower tripping the mcb less frequently. the shower is a mira sport 9.5kw. Has anyone got any ideas what could be causing the mcb to trip in such a random way.
I have inspected the cable for signs of damage but found none, mcb is a cpn B40 on a dual RCD board. Insulation resistance on the circuit is >299 Mohms between L/N, L/E, N/E. R1 + R2 is o.21 ohms. Zs 0.71 ohms. I checked the pulll co isolator and it showed some signs of heat damage, so replaced that which resulted in the shower tripping the mcb less frequently. the shower is a mira sport 9.5kw. Has anyone got any ideas what could be causing the mcb to trip in such a random way.