Putting the shower pump for an aqualisa quartz digital system in the wardrobe of the bedroom behind the bathroom. There is already a single plug socket in there.
In the instructions it says to connect to a 3A fused spur unit with no rcd.
I propose to change the socket to a fused 30ma rcd unit anyway to be safe as the main board is only protected by an old hager rccb which is 100ma.This will also provide discrimination on the circuit.
Does it need protection as will be connected by plastic piping to the shower and it is installed outside of all zones?
Regards