Just been reading through this?
Bit confused as to what exactly has been tested.. or proved..
and in what order?
is this your beastie..
Electric Showers
https://ww2.tritonshowers.co.uk/webapp/wcs/stores/servlet/CategoryDisplay?storeId=10001&catalogId=10001&top=Y&categoryId=10051
Thought I read that you had proved a fault on the can.
then replaced it..
but then fault still there so not proved???????
If water is part of the earth bridge path..
then all testing MUST be done with the water in the system..
BUT I would also have cables physically removed from the shower terminals to proved no fault path back up the incoming 6 or 10mm..
Anyway...
Does the shower ALWAYS trip immediately on ALL settings?
e.g. A Typical electric shower has 3 operating settings...
(a) Cold - No heat elements in circuit..
(B) Heat#1 - One heat element in circuit..
© Heat#2 - Two heat elements in circuit..
so..
What happens if you run it on the COLD ONLY setting?
What happens on Heat#1
What happens on Heat#2
may help eliminate if it is a specific single component?
Have you actually opened up an proved 110% that the shower isolator switch is OK?
It is VERY common for the isolator switches to have screw terminals that are not tight..
thus joints heat up.. conductors get warm..
Insulation starts melting a bit....
Then possibly making contact with an earth (CPC) wire bunched in the back of the isolator switch?
So as the shower draws power.. cable heats up..
Earth path made..
then cools down again later and fault path then disappears!
{Above points assuming typical ceiling cord pull isolator switch..}
Cant see any actual resistive readings from any of your tests?
i.e. what is the ohms values from your continuity and insulation resistance tests?
Are you aware of the typical values you get if reading through a Neon indicator..
Is this RCD only connected to the shower?
or does it protect other circuits as well?