Did a favour job last week, and swapped out a faulty one, driving an extract fan for a hotel kitchen.
However, they`ve had three times this week, when the fan stops. Drive shows an error code ( maybe F02) - voltage out of spec.
I`ve since spoken to the guy whose job it is - he went out to the old drive with errors - found a melted connector on L2 supply, and remade the terminations.
So I`m wondering.............
If the fan motor is failing / leaking at running temp, and trying to draw more power - could that be the cause?
OR....Given the physical location of the actual motor unit, I don`t believe it gets cleaned regularly - two other 12" ducts would have to be dismantled, 4 floors up (internal to building, in a service riser), before being able to access the fan motor.
It isn`t my bag - I simply copied the settings from the original drive onto the new one - but he`s asking me, as its on the fringes of his knowledge.
My initial suggestion is to go and clamp the phases, and see if one is drawing an imbalance.
My questions are twofold:
1. I`m assuming that I`ll get much more info from the drive, if I were to connect it to the lappy, rather than using the BOP? I understand the s/w is freely available, but the connecting cable is special (but I think a local member on here has one?).
2. At the moment, when the drive errors out, they have to go to the 4th floor service cupboard, and operate the local isolator, to reset the drive. Is there an option to have the drive do a manual reset under fault condition? Can it be done from the BOP, or would it need the s/w?
Thanks all
KME
Did a favour job last week, and swapped out a faulty one, driving an extract fan for a hotel kitchen.
However, they`ve had three times this week, when the fan stops. Drive shows an error code ( maybe F02) - voltage out of spec.
I`ve since spoken to the guy whose job it is - he went out to the old drive with errors - found a melted connector on L2 supply, and remade the terminations.
So I`m wondering.............
If the fan motor is failing / leaking at running temp, and trying to draw more power - could that be the cause?
OR....Given the physical location of the actual motor unit, I don`t believe it gets cleaned regularly - two other 12" ducts would have to be dismantled, 4 floors up (internal to building, in a service riser), before being able to access the fan motor.
It isn`t my bag - I simply copied the settings from the original drive onto the new one - but he`s asking me, as its on the fringes of his knowledge.
My initial suggestion is to go and clamp the phases, and see if one is drawing an imbalance.
My questions are twofold:
1. I`m assuming that I`ll get much more info from the drive, if I were to connect it to the lappy, rather than using the BOP? I understand the s/w is freely available, but the connecting cable is special (but I think a local member on here has one?).
2. At the moment, when the drive errors out, they have to go to the 4th floor service cupboard, and operate the local isolator, to reset the drive. Is there an option to have the drive do a manual reset under fault condition? Can it be done from the BOP, or would it need the s/w?