I had a similar but not identical issue with Solis hybrid and Solic200.
What would happen was this.
Solic would detect a minor overshoot of export as inverter settled after a load change (say kettle clicked off).
Solic would grab this very fast and direct it to immersion.
Next, Inverter sees this as as a new load and ramps up output, using battery if necessary.
Somehow this would slowly spiral and the system would end up with a constant 2.5kw flowing from battery to immersion until battery was exhausted.
My temporary fix which may become permanent is this:
I've taken the "live" out from solic200 and passed the single, double insulated cable, through the inverter's CT clamp. In a direction such that the CT sees current going to the immersion as export. Which from the inverters point of view, it is.
So now the inverter, in effect, ignores anything the solic does and acts just like it did before solic was installed.
While solic grabs any export and directs it to the immersion.
It actually appears to work perfectly, far better than I expected. I appear to have set up a hierarchy. Solar generating to house first, batteries second and immersion only when there's more than the other two can take.