OK, there's never been a requirement to earth panels or framework except where you have Micro-inverters behind the panels, on TN-C-S, which means you have AC cabling behind the array itself, and the metal framework represents an 'extraneuos conductive part' ie a short could make it live. Guidance may have changed since I last read that, but no real explanation was ever given as to why.
As you have a ground array (I'm assuming it's steel) you have lots of earth rods in the ground already. If you wanted to make sure you have a good earth, I would use copper strip, as per ligtning conductors rather than a rod, and galvanised self tapping screws to connect to the frame. I would connect steel armour of the SWA to the frame, but not the inverter end. Your inverter is on the side of your house, so connect that to the house earth. With TN-C-S we are not allowed to 'export' the earth to another building away from the property, which is where TTing a shed or garage comes from. I wouldn't be looking to connect house earth and framework (earth rod). Given a faulty Neutral in your house supply, you could find your frame becomes live. Your inverter will look for DC faults every morning as it starts up, in particular it looks for shorts to earth, known as RISO in the PV industry. Anything less than 20 MOhms and it won't start up.
I've worked on many solar farms, these are not earthed on the DC side. I would install a DC isolator at the array end of the SWA, (you need something to terminate the SWA to anyway) so in the unlikely event of damage to the SWA, you can isolate it to work on.