SolaX Triple Power Battery Balancing

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

spacemoc

New member
Joined
Sep 28, 2024
Messages
3
Reaction score
0
Location
Northamptonshire
There appears to be a lack of information available on how to properly balance SolaX batteries. Here are the steps:
  1. Force discharge the batteries down to 10%.
  2. Shut down the master battery and disconnect the slave battery.
  3. Short the master battery, then reconnect it to the inverter and power it back on. You should see a state of charge (SOC) on the inverter that is significantly higher than 10%.
  4. Discharge the master battery down to 10%.
  5. Once complete, reconnect the slave battery and return the system to normal operation.
At this stage, both batteries should be at the same SOC (10%).

However, there is one issue: the master battery will not operate without at least one slave. So, how does one balance the master and slave when only two batteries are available?
 
Top