Is there a reason you don't want to supply the second board with 25mm tails? Or am I missing something?i need to split the tails to add an additional consumer to run a radial socket circuit & lighting circuit. will it be ok to provide this consumer unit with tails 4mm or 6mm Cheers
small board? and shear size of cables trying to terminate them maybe?Is there a reason you don't want to supply the second board with 25mm tails?
Is overcurrent protection not coming from the service fuse if he's splitting the tails - so 6mm tails on a 80A/100A fuse.small board? and shear size of cables trying to terminate them maybe?
you dont as it happens,as you have to take 25mm to the main ccu
no, not over a short distance, they can be fused at either end,Is overcurrent protection not coming from the service fuse if he's splitting the tails - so 6mm tails on a 80A/100A fuse.
So you're going to run 6mm Line & Neutral - because it could be hard to terminate 25s..........but you're going to run a 16mm earth?keep all your earths the same size,ie, if your largest earth is 16mm, then make the earth to all your CUs 16mm, not including MEBs or supplementaries of course.
The OP might insist that the CU will only ever serve the circuits he has suggested - but the fact is, it's possible for 6mm tails to be overloaded with the setup he describes.no, not over a short distance, they can be fused at either end,
this is one of the reasons (apparently) that the DNO has a max distance/length of tails permitted.
No - he's going to bang a rod in.So you're going to run 6mm Line & Neutral - because it could be hard to terminate 25s..........but you're going to run a 16mm earth?
Yes, but that 1mm twin wouldn't be coming off a henley block connected directly to the tails - it would be connected to a suitably rated MCB, that would trip first.correct me if I am wrong, but the fault current on your 25mm tails in the CU would be near enough the same as the fault current say on a 1mm twin supplying a spur right next to the CU.
Are you sure? When we moved in to our house we had 16mm tails on a 80A fuse (verified). I thought the tails belonged to the homeowner, not the DNO. Mine were upgraded when we got the CU changed.If you ask the DNO to upgrade the service fuse from a 60A to an 80A, they will change the tails from 16mm to 25mm - now, they'll do this regardless of whether you have a 2-way, 4-way or 16-way CU attached to the end of them, and regardless of what rating of MCBs you have in the CU........why?