Sidewinder I found this in Gn 8 the green book and it was not updated to the new amended edition.
I looked for that reg; could not find it.
Gn 8 Page 29Re TN-C systems;
This system type is very infrequently used in the UK.
Reg; 546.02.01 of BS 7671 restricts the use of an installation
PEN conductor to circumstances where;
as required by ESQCR the consumer has obtained an exemption
from the ban on CNE conductors in the installation or;
The source is a privately owned transformer or generating plant
or other source and connected in such a manner that there is
no connection with the public distribution system.
Technician,
There is no GN8 related to the 17th Ed at all.
The current version of GN8 is a 16th version, yes it has a green cover, they all will, the 8 is in a brown circle.
They never updated GN8 to the red book, they are currently updating it to the 17th Amd1, it is due for publication in April 2012.
You have misread and mis quoted the regs mate, sorry.
You have transformed reg 546-02-01 to reg 546.02.01, the first is a 16th reg, the 2nd is a non existent 17th reg.
The dashes in GN8 are a dead give away that it is a 16th or before reg, as from the 1st Ed. of the 17th the dashes were changed to dots.
546-02-01 refers to 546-02-02 to 546-02-08, and then goes on...
This reg when changing from the 16th brown book to the 17th red book the reg. went from 546-02-01 to 543.4.2 & now refers to regs 543.4.3 to 543.4.9
The wording is similar between the two books, though there are some differences.
There are also some changes between the 17th Ed. red & green books with respect to Reg. group 543.4
I understand the differences in the systems, my request for a reference was urgent as I had to go on site to check out a machine the following morning, that the client stated was using a TN-C system in the machine wiring.
This did not turn out to be the case.
I also did not need to convince the client it was wrong, to have TN-C in their install or their machine, they were very concerned about this themselves.
As it turns out, the system was not TN-C anyway.
There was no N conductor of the supply at the machine it was TP&E only.
HTH.