Here is what I currently see as a strange situation. Though I am hoping that with the responses of a few brain boxes, it will be cleared up.
Was doing some testing today and went to IR test a circuit (Upstairs Sockets). I had disconnected everything and even checked that there wasn't a booster, etc in the loft. Still airing on the side of caution I did a 50v (L-N) to cpc. Got 35.6 Meg Ohm.
Instant thought 'ooer, this aint right'. did it on 100v and got 66.3 meg Ohm. tried 250v and got >200.........
No, by reconning, those results sound the wrong way round. Surely the more pressure you put behind a insulation breakdown, the more it will give. I would expect a lower reading with higher voltage.
Obviously being dumb and missing something.
Please enlighten