Evening,
as part of a job the dno ( UKPN)
have installed a 100a tp&n supply in a feeder cabinet typical tnc-s supply.
i have run a 50mm 5c swa to a new shop and terminated in a mem 3ph db.
on the supply end I have terminated the 50mm into a 100a isolator and left 25mm tails for the meter provider.
he came yesterday and won’t connect as “ it needs to be a switch fuse “
I said why ?
he said because it does.
i am certain it complies.
comments please ( Bare in mind I’ve got the Reg numbers to support my claim)
thanks in advance.