Im currently in the forces and employed as a sparky, we currently use a system call LAPDS made by a company called blakley, when it comes to inspection and testing we have a headache.
so, we use a generator as source, then distribute 3 phase down through modules to single phase to a final module that will have either 16 amp iec sockets or weatherproofed 13 amp sockets,
the cables are all made by us and pat tested by us, the modules are all inspected by us as per the manufactures instructions as is the generator. The modules all have either 63, 32 or 16 amp RCD/RCBO circuit breaks on there outputs.
Before we do anything we fully design the system producing a full area plan to scale showing where every cable and module is laid and then a linear plan showing the full connectivity of the plan, as well as this we also work out, for every cable:
Design current, protective device, Voltage drop, Zs max, Zs, R1/R2, Pfc, cable burn out time, min CPC size,
It is then cabled together as per the plan, then all final distribution is RCD tested recording all the trip times
Do we require to carry out anything else to make sure we are on the correct side of the law
any advice would be helpfull
regards
steve
Im currently in the forces and employed as a sparky, we currently use a system call LAPDS made by a company called blakley, when it comes to inspection and testing we have a headache.
so, we use a generator as source, then distribute 3 phase down through modules to single phase to a final module that will have either 16 amp iec sockets or weatherproofed 13 amp sockets,
the cables are all made by us and pat tested by us, the modules are all inspected by us as per the manufactures instructions as is the generator. The modules all have either 63, 32 or 16 amp RCD/RCBO circuit breaks on there outputs.
Before we do anything we fully design the system producing a full area plan to scale showing where every cable and module is laid and then a linear plan showing the full connectivity of the plan, as well as this we also work out, for every cable:
Design current, protective device, Voltage drop, Zs max, Zs, R1/R2, Pfc, cable burn out time, min CPC size,
It is then cabled together as per the plan, then all final distribution is RCD tested recording all the trip times
Do we require to carry out anything else to make sure we are on the correct side of the law
any advice would be helpfull